Please login or register.

Login with username, password and session length

Author Topic: X10 AM12W (appliance module) connection to a relay  (Read 29630 times)

2006x10

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 6
X10 AM12W (appliance module) connection to a relay
« on: October 22, 2006, 07:37:55 AM »

I just installed a few appliance modules AM12W and AD10 for my lighting automation. I also installed a AM12W (to a 230Vac relay) for my motor driven gate control. The lighting controls worked well, but the relay for the gate kept buzzing when AM12W was at "OFF" position.

The connection to the relay:
Brown wire was connected to "L", black wire to the relay coil, blue wire to "N". The other terminal of the relay coil was connected to "N".

The problem:
The relay kept buzzing when the AM12W was at "OFF" position.

When AM12W was at "ON", the relay operated correctly.

Anyone knows whether the AM12W leaks some voltages to the relay? I changed a AM12W, the relay behaved the same. Possible to suggest a workable connection?

I did try with a UM7206, but it did not work with my DSC security system.

Thanks for the help.

Logged

Dan Lawrence

  • Hero Member
  • *****
  • Helpful Post Rating: 68
  • Posts: 3991
Re: X10 AM12W (appliance module) connection to a relay
« Reply #1 on: October 22, 2006, 09:36:10 AM »

You are not in the United States or Canada, are you?  Both the AM12W and the AD10 are modules for Europe and the rest of the world., not for US/Canada use.
Logged
I don't SELL this stuff... BUT I sure do ENJOY using it!!!

2006x10

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 6
Re: X10 AM12W (appliance module) connection to a relay
« Reply #2 on: October 22, 2006, 10:14:27 AM »

I am living in Singapore/Malaysia. The power system here is the same as the system in UK.

I saw some posts elsewhere talking about current sensing in appliance module and the method to disable the feature. Any idea whether current sensing can be disabled for AM12W?

Thanks.
Logged

Charles Sullivan

  • Hero Member
  • *****
  • Helpful Post Rating: 94
  • Posts: 1565
    • HEYU - X10 Automation for Linux, Unix, and Mac OSX
Re: X10 AM12W (appliance module) connection to a relay
« Reply #3 on: October 22, 2006, 10:18:57 AM »

According to the Marmitek (http://www.marmitek.com) FAQ:

   Product: AM12 Appliance / Switch Module Art. nr. 08915
   Question: Can I switch off the auto-senso function?
   Answer:
   You can do this by loosening pin 7 of the IC. Attention: this will forfeit your guarantee.
   Module with a production code higher than 04Dxx don't have Auto-sense. The label will mention "Low energy lamp compatible"
Logged
Yesterday it worked.
Today it doesn't work.
X10 on Windows is like that.

HEYU - X10 Automation for Linux, Unix, and Mac OS X     http://www.heyu.org

KDR

  • Hero Member
  • *****
  • Helpful Post Rating: 53
  • Posts: 758
    • Home Automation Chat
Re: X10 AM12W (appliance module) connection to a relay
« Reply #4 on: October 22, 2006, 10:23:15 AM »

Take a look here http://www.idobartana.com/hakb/index.htm there is info on mods for appliance modules. You may have to take a look inside to see if it is the same or not. Its a start ;D
« Last Edit: October 24, 2009, 12:30:32 AM by -Bill- (of wgjohns.com) »
Logged
Note: "Guests" may read the X10 forum , but you must register to post!

When I'm online you can find me in the Home Automation Chat Room!

2006x10

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 6
Re: X10 AM12W (appliance module) connection to a relay
« Reply #5 on: October 22, 2006, 10:54:31 AM »

Quote:
   You can do this by loosening pin 7 of the IC. Attention: this will forfeit your guarantee.
   Module with a production code higher than 04Dxx don't have Auto-sense. The label will mention "Low energy lamp compatible" 
 Unquote:
   
Thanks for the info. The production code on my AM12W in question is 9B07. I do have a few with production code greater than 04Dxx. I will try to swap 1 to see the outcome.
 
Thanks for your help.
Logged

2006x10

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 6
Re: X10 AM12W (appliance module) connection to a relay
« Reply #6 on: October 22, 2006, 10:58:43 AM »

Quote:
Take a look here http://www.idobartana.com/hakb/index.htm there is info on mods for appliance modules. You may have to take a look inside to see if it is the same or not.
Unquote:

The appliance module shown in http://www.idobartana.com/hakb/index.htm is different frm the one I have. Thanks for your help.
« Last Edit: October 24, 2009, 12:29:53 AM by -Bill- (of wgjohns.com) »
Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13260
Re: X10 AM12W (appliance module) connection to a relay
« Reply #7 on: October 22, 2006, 01:12:16 PM »

Lifting pin 7 will disable the local sensing control, but not stop the current from buzzing the relay. Not sure on a AM14W how to disable the physical current. many times it is a few resistors and a diode.
Logged

KDR

  • Hero Member
  • *****
  • Helpful Post Rating: 53
  • Posts: 758
    • Home Automation Chat
Re: X10 AM12W (appliance module) connection to a relay
« Reply #8 on: October 22, 2006, 02:06:09 PM »

Try this site also  http://www.automatestuff.com/

It talks about the AM12W specifically and how to disable local sensing pics included. (About the same as Brian and Charles posted)

Here is another page that talks about the problem  http://board.homeseer.com/archive/index.php/t-112193.html

Hope some of this helps. I'm looking for a print on the AM12W and if I find anything I will post it back here.
« Last Edit: October 22, 2006, 02:26:06 PM by KDR »
Logged
Note: "Guests" may read the X10 forum , but you must register to post!

When I'm online you can find me in the Home Automation Chat Room!

2006x10

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 6
Re: X10 AM12W (appliance module) connection to a relay
« Reply #9 on: October 23, 2006, 04:44:58 AM »

Thanks KDR, Brian, Charles and Dan.

I tried with a 10kohm 20W resistor across the relay coil, and the buzzing noise stopped. I think I like the idea of connecting a night light (or indicator light) in parallel to the relay better, since the light will indicate the contact catching of the relay.

Really appreciate everyone's help. Thanks again.
Logged
 

X10.com | About X10 | X10 Security Systems | Cameras| Package Deals
© Copyright 2014-2016 X10.com All rights reserved.