Please login or register.

Login with username, password and session length
Pages: 1 2 [3]

Author Topic: Phase Coupler  (Read 21623 times)

marineau

  • Hero Member
  • *****
  • Helpful Post Rating: 2
  • Posts: 162
Re: Phase Coupler
« Reply #30 on: December 16, 2006, 06:26:26 AM »

Puck:

You have probably reason, My furnace of heating have a 100A breaker and Main is 200A...
I have 20KW element heater inside my furnace. 20,000 / 240 = 83.3Amp

Other exemple: my Refrigerator have a 15A breaker, but his real load is 4Amp

So Truth, each circuit breaker was only installs to protect each one of their wire, and we can't adding all breaker value to know a total capacity but just Theoretical.

Now, we can't forget that our Main Breaker 200A are installed to protect our Main Wire connected to our electricity Company distributor !

Logged
Pages: 1 2 [3]
 

X10.com | About X10 | X10 Security Systems | Cameras| Package Deals
© Copyright 2014-2016 X10.com All rights reserved.