mikeythemars:
This may seem like a very basic question, but I am planning on installing an XPCP passive coupler and want to be sure I am clear on the connections between the breakers on the board and the unit. 

Specifically, the PDF online that shows the install instructions for the XPCP states that it requires 240 VAC.  The graphic on the instructions shows that power connection (labeled "LI" and L2")  coming from what appears to be a double throw breaker pesumably wired for 240V.  What I want to know is if I can connect those two lines to two separate single throw 20 AMP breakers (one on Phase A and the other on phase B), each supplying 120volts to the XCPC.   Presumably, that would be replicating what the double throw breaker in the instructions is doing.   The reason i'd like to do this is I have two open breaker slots at the top of the board, which would allow me to have the XPCP connected to dedicated breakers (no double taps,  which are against code).   I do not have any have any open space on the board for a new double throw breaker.             

Knightrider:
I'd just slide some single pole breakers around till I had a double pole space available.  What you propose can be done, but probably shouldn't. Fire investigators look at such things, even if such a configuration had nothing to do with a fire.

mikeythemars:
Thanks Nightrider.  I can move some breakers to open up a double pole position.    I assume the point you are making is not having two separate breakers supplying a single 240 VAC device.   Frankly, the instructions X10 has up show another issue, which is someone assuming based on the illustration that they can double up wires to an existing 240VAC breaker.  If their assumption was someone was going to already conveniently happen to have an unused double pole breaker on their board or install a new one that could be solely dedicated to the XPCP,  they should have stated that (all the install instructions say on that matter is "connect L1 terminal to L1 breaker terminal and L2 terminal to L2 breaker terminal."   

brobin:
While you can't put two wires under the same screw terminal of a breaker (unless the breaker is specifically listed to accept two wires), the NEC does allow a pigtail from the breaker to multiple wires using a properly sized wire nut.  The reason for not allowing two wires on the terminal is possible arcing or overheating from a poor mechanical connection.  As for using two single breakers for a 240 circuit, that's ok ONLY if there is a clip or bar connecting the two handles so that if one trips the other will shut off as well. Of course, they still need to be adjacent to do that.  The reason for that is so that if the protected appliance trips a breaker you won't still have 120 present at the appliance.  Bottom line - if you have room for the dedicated breaker for the XPCP that would be best but if not you can use a pigtail to serve both the appliance and the XPCP.  If you do that, try to avoid using a circuit with a high startup draw like an AC condenser and instead use a dryer or oven breaker.  Years ago I used a UL listed bridging capacitor across the breaker for an AC condenser in a panel in our bedroom closet.  At about 4:30 one morning we were awakened by what sounded like a gunshot.  Scared the crap out of us!  Apparently, when the AC kicked on the cap exploded with such force that there was soot on the wall along the outside edge of the panel cover. The breaker didn't even trip.  Lesson learned!

Brian H:
I would look at the breaker mapping. Usually on the panel or its cover. If it was two slots for 1/2 Sized breakers. It is possible both slots are on the same line input.