I have had good success using the firecracker starter kit. But I get a 6/7 sec. delay from the Palm Pad Remote Control to the Lamp Module. Is anything I can do ti fix it or it takes that much time to turned them off/on?
The Firecracker Starter Kit I'm familiar with is this one:
http://www.x10.com/automation/ck18a_s_ps32.html Is this what you have?
If so, then the PalmPad should be sending an RF signal to the TM751 Transceiver and the TM751 should be transceiving this to a powerline signal which turns On the Lamp Module. The delay between pressing the button on the PalmPad and the lamp turning On should be no more than about 1 second.
Let's start with the RF signal from the PalmPad to the TM751:
If you press the On and Off buttons for Unit #1 on the PalmPad, you should almost instantly hear loud clicks from the TM751's built-in appliance module relay. Do you? (Try it with the PalmPad no more than 2 or 3 feet from the TM751.) If it takes several seconds for the audible click, possible problems could be:
1. Defective PalmPad (Does the LED on the PalmPad flash steadily when you hold down the button?)
2. Defective TM751
3. Unusually high level of RF interference from some other appliance. (This would be rare at that frequency).
If I correctly infer from your message that turning the Lamp module On and Off using the Firecracker module and X10's Firecracker software from your computer works fine, then I'd conclude you probably have a defective PalmPad.