🖥️ActiveHome Pro => Plug-ins => Smart Macros => Topic started by: PajamaGuy on December 11, 2008, 08:23:16 AM
-
14075 12/10/2008 22:57:31 PM Receive RF MS-Liv - Motion Reset
14076 12/10/2008 22:57:31 PM Receive RF MS-Liv - Motion Reset
At this time FLAGs 1 & 10 are OFF, F1 and F10 (monitored) are OFF
Macro triggered on F6=OFF which is timed to OFF at 23:00
14077 12/10/2008 22:59:48 PM Receive L9 (StairsLight)
14078 12/10/2008 22:59:49 PM Receive L Off (StairsLight)
Macro triggered on M1=OFF which is timed to OFF at 23:00
Not shown – FLAG#1=CLEAR, FLAG#10=SET
14079 12/10/2008 22:59:49 PM Receive F1 (Day/Night Flag)
14080 12/10/2008 22:59:50 PM Receive F Off (Day/Night Flag)
14081 12/10/2008 22:59:50 PM Receive F10 (Wake/Evening Flag)
14082 12/10/2008 22:59:50 PM Receive F On (Wake/Evening Flag)
Should have DELAYed 10 Seconds
14083 12/10/2008 22:59:51 PM Receive O1 (ResetAllLights)
14084 12/10/2008 22:59:51 PM Receive O On (ResetAllLights)
The following is Conditional on FLAGS#1&10 being OFF but it runs as though both 1 and 10 are OFF
14085 12/10/2008 22:59:52 PM Macro L All Units Off
14086 12/10/2008 22:59:57 PM Macro L1 (DiningLamp)
14087 12/10/2008 22:59:57 PM Macro L Bright 100(DiningLamp)
14088 12/10/2008 22:59:57 PM Macro L Dim 26(DiningLamp)
14089 12/10/2008 22:59:58 PM Macro L9 (StairsLight)
14090 12/10/2008 22:59:58 PM Macro L On (StairsLight)
14091 12/10/2008 23:00:04 PM Macro L3 (DWA Bed Lamp)
14092 12/10/2008 23:00:04 PM Macro L Bright 100(DWA Bed Lamp)
14093 12/10/2008 23:00:04 PM Macro L Dim 71(DWA Bed Lamp)
14094 12/10/2008 23:00:05 PM Receive L All Units Off
14095 12/10/2008 23:00:11 PM Macro L7 (OfficeLamp)
14096 12/10/2008 23:00:11 PM Macro L Bright 100(OfficeLamp)
14097 12/10/2008 23:00:11 PM Macro L Dim 67(OfficeLamp)
There is an L8 On & Dim 65% here that does NOT execute
14098 12/10/2008 23:00:12 PM Receive F6 (KeepStairlightON)
14099 12/10/2008 23:00:12 PM Receive F Off (KeepStairlightON)
F6=OFF triggers another macro (I need to fix this)
14100 12/10/2008 23:00:13 PM Macro L9 Extended Code 16 31 (StairsLight) L9 is an appliance module and there is NO dim command
14101 12/10/2008 23:00:14 PM Receive D6 Extended Code 1c 31
============================================
I tried firing the macros with their own timer, and I've tried using a timed phantom - same result. What gets me is that the DELAY doesn't happen. O1 has 4 conditional ELSES depending upon the status of the FLAG#1/FLAG#10 condition, so I put the DELAY of 10 seconds in the FLAG-setting macro to ensure there was time for them to register the FLAGs before the O1 macro looked at them for a condition. M10 is simple - Phantom M10 turns OFF at 23:00 via timer. Macro M10-OFF is triggered by the phantom going OFF, and it CLEARs FLAG#1, SETs FLAG#10, sets F1=OFF, and F10=ON ("F" is monitored) then it is supposed to DELAY 10 seconds before flipping phantom O1=ON.
Can it be failing because I'm flipping 2 phantoms, and therefore 2 macros both at exactly 23:00? And yep, tonight one of them is moving to 23:05.
-
PJ,
If you are running AHP V3.326 I believe it's the culprit here.
I do not understand the following "receives" (these should all be transmit statements), but saw something similar when activating a simple AM466 appliance module using V3.326.
14075 12/10/2008 22:57:31 PM Receive RF MS-Liv - Motion Reset
14076 12/10/2008 22:57:31 PM Receive RF MS-Liv - Motion Reset
At this time FLAGs 1 & 10 are OFF, F1 and F10 (monitored) are OFF
Macro triggered on F6=OFF which is timed to OFF at 23:00
14077 12/10/2008 22:59:48 PM Receive L9 (StairsLight)
14078 12/10/2008 22:59:49 PM Receive L Off (StairsLight)
Macro triggered on M1=OFF which is timed to OFF at 23:00
Not shown – FLAG#1=CLEAR, FLAG#10=SET
14079 12/10/2008 22:59:49 PM Receive F1 (Day/Night Flag)
14080 12/10/2008 22:59:50 PM Receive F Off (Day/Night Flag)
14081 12/10/2008 22:59:50 PM Receive F10 (Wake/Evening Flag)
14082 12/10/2008 22:59:50 PM Receive F On (Wake/Evening Flag)
Should have DELAYed 10 Seconds
14083 12/10/2008 22:59:51 PM Receive O1 (ResetAllLights)
14084 12/10/2008 22:59:51 PM Receive O On (ResetAllLights)
-
Thanks! I believe I was running 228 (and am now) - I found the CM15 was "remembering" even after clearing and I think I didn't leave the batteries out long enough. Also, it appeared the macros addressed as "M"' screwed things up. When not using M as their address, things worked better.
If I can find it, I'll go back to 204. For now, Merry Christmas!
-
Thanks! I believe I was running 228 (and am now) - I found the CM15 was "remembering" even after clearing and I think I didn't leave the batteries out long enough. Also, it appeared the macros addressed as "M"' screwed things up. When not using M as their address, things worked better.
If I can find it, I'll go back to 204. For now, Merry Christmas!
Well V3.228 was not without some idiosyncrasy's of its own. Especially if you were running with the V3.326 Driver patch. I honestly didn't spend much time delving into this.
If you do encounter some wild activity (as you did above), please PM me and send the "ahpeeprom_w.txt". This is typically located under "C:\Documents and Settings\All Users\Application Data\Active Home Professional" for WinXP.
I'd love to see what AHP is instructing the CM15a to do.
Boiler