x10 (PLW01-i) blows when I turn on the light with it. Replace it, it blew, and still again. I had the one swith for years. 4 years on this outside light on the power pole. The bulb is a 300watt. That's the only thing on this switch. Since it's an outside light, do you think it's a short between the switch and the light. I know they are only rated at 500w so I keep way below that. Been fine for this light for about 4 years.
Ideas, suggestions. :)
Thanks
John
-
That isn't on the pole that your electric feeder comes from? There may be leakage that's fouling your PLW01-i s if it is. I would never use anything X10 on a pole where my electric feeder is also on it.
-
It is a possibility. There is a short between the switch's location and the light.
Since it is outdoors. You may also want to verify the light fixture itself doesn't have a failure in it.
-
Since it's an outside light, do you think it's a short between the switch and the light.
Yup. You got "a short in the socket" so to speak.
If you are handy with a soldering iron you can probably repair the two blown units by replacing the triac. Radio Shark used to carry a 5A, 600V, pin compatible replacement.
-
Thanks for your input. :)
I put a regular switch on there just to try it. Trips the circuit breaker in the box instantly. Yep, got a short.
I'll have an electricion find the short. Try replacing the triac myself just for the experience but put a new PLW01-i on there anyway.