🖥️ActiveHome Pro => ActiveHome Pro General => Help & Troubleshooting => Topic started by: Hugh W on December 06, 2011, 07:59:46 PM
-
I have had a working X10 system for external lights for several years.
We just got a second oven installed that required a new breaker (20amp double pole).
Since then the lights stopped working.
I tripped the circuit breaker yesterday and everything started working again.
Not sure why the oven would break my system.
Can anyone offer a suggestion?
The interface is a CM15a
-
It's possible the new oven is to blame. Either it puts noise on the powerline (a distinct positive given when you tripped the breaker X10 started working). You probably need a filter on the circuit the oven is on. Do a search here for filters and see what's usable. You will need to have the power draw amount to get the right filter.
-
Not sure why the oven would break my system.
Can anyone offer a suggestion?
The interface is a CM15a
Most likely it uses a (noisy) switching power supply for the electronics. You might try an XPNR (X10Pro.com) since it wires across the load and not in series, like most filters. Also do you have a repeater? Sometimes they can boost X10 signal above the noise.
-
Thank you - I will attempt to find a Filter. I do not have an extender, I do have a Coupler/Repeater that I did not install since prior I did not need it. (No spare slots in the circuit panel now)
-
Solved - I swapped the two HOT wires on the Circuit breaker. Everything started working again.
-
So whatever was putting out the noise is on the OTHER phase from the affected modules, most likely.