Thanks for the reply. I just don't know if I should keep dumping money into this as it seems like the only way to troubleshoot is to keep buying parts until it either works or doesn't. By that time, I could have just bought a system specifically designed for what I want to do and spent less money. In reading, I think the next thing I would need to buy would be a coupler/repeater. That's another $100. You see what I mean.....where does it end?You shouldn't need a coupler /repeater for a vaction home. Refrigerators Are to be on there own recepticle with nothing else same as a microwave oven, puting the module on the same recepticle is asking for problems as you've seen.
How big is the cabin?
How are you controlling your "a/c- heater with an appliance module?
Have you added any electronics in the cabin since that time that the system worked?
Can you plug the BoosterLinc and Telephone responder into the same branch circuit as the appliance module? If this isn't possible, at least get the Boosterlinc and the Telephone responder on the same circuit.
If you "unplugged everything in my house and still nothing" then it likely isn't a noise problem unless it is coming from a 240V appliance, or something new that is hard wired. If it isn't noise then a coupler / amplifier should help. You might also try the Smarthome signal level meter. It WILL tell you if it is noise and help you pinpoint the source.
You shouldn't need a coupler /repeater for a vaction home
QuoteHow big is the cabin?
1200-1500 sq. ft.
I have since installed my coupler/repeater and I am still having the same problem. That makes this project well over $250 and I still do not have any success. I have tried everything that was recommmended on here, with no change in status. It apprears that the alarm system is sending out the signal, because when I push the test button on the coupler repeater it blinks and goes steady when I send the signal. The universal module is working manually, but I don't believe it is receiving the signal. Could it be a faulty module that allows it to work manually and not receive signals? I am at my witts with this sytem and I don't want to spend another dime. What should I do next?
The module is approximately 15' from the controller. As far as the coupler/repeater being installed, I installed it like it was shown on the diagram from leviton. Two breakers side by side. Is there another way I am suppose to install it? Like I said, I tested the coupler repeater and it was working properly (it was receiving x10 signals).
Don’t make the mistake that is often made by DIY’ers and even some electricians. They wire the double-breakers as shown in Figure 7 which causes the passive coupler to be wired from one leg and then right back to the same leg. That doesn’t help much. Instead, the passive coupler needs to be wired as shown in Figure 8.(http://www.act-solutions.com/images/hti807.jpg)(http://www.act-solutions.com/images/hti808.jpg)
Good news...I just got a call from my alarm company who said the system is now working flawless. The alarm wasn't programmed correctly.
However, I am curious if the electrician wired my coupler/repeater properly. Here is what he did. 1 dual pole 20 amp breaker. One hot to one and one hot to the other, neutral to neutral. The directions called for two separate 15amp breakers, however, this is what I got. Is it wrong? Remember this is my vacation home, so I can't just go and check on things right away. I will probably be out there again in several weeks.
1 dual pole 20 amp breaker. One hot to one and one hot to the other, neutral to neutral. The directions called for two separate 15amp breakers, however, this is what I got. Is it wrong?
It is taking up two slots, however it only has one trip lever on it and it is 20 amps. The guy messed up when he bought the breaker, but I had it installed like that anyway. What I wanted was two 15 amp breakers that take up their own slot (that was what the instructions called for). If it is wired incorrectly, I can always change it myself. So once again, is it installed incorrectly? You guys are a wealth of knowledge...
ArtClark; Not in my older homes breaker box. I have like 4 breakers; in a row from top to bottom all on the same phase then the next 4 are the other one. Only a few positions next to each other are 220 across the breakers connection screws.