🖥️ActiveHome Pro => ActiveHome Pro General => Help & Troubleshooting => Topic started by: PLCGuru on January 16, 2011, 06:30:21 AM

Title: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 16, 2011, 06:30:21 AM
Been using X10 since the end of the Disco era  ;)   So I know the limitations of X10.  I know about finding noise, filtering noise, signal suckers, line couplers, RF TX & RX units, repeaters, JV's XTB, neighbours with similar house codes, low batteries in motion units sending codes, etc.
I recently replaced my CM11, which was working flawlessly with AH for the last 8 years.  I upgraded to the CM15A and AHP version 3.301.  I have a very simple system, 9 modules and 2 macros.  The macros work great. This is my problem.  After observing my new system for the last 4 weeks, I think I have a defective CM15A.  In the middle of the night, when all modules in the house are off, I sometimes get a randon turn-on of module P1.  This is with the CM15A NOT connected to my computer.  If I clear the memory, remove batteries and reprogram, I'm good for a few days.  After a few days, I start getting other modules randomly starting in the middle of the night.  Clear the memory again, same scenario, but now I wake up to a different module number that has randomly turned on.   If I run the CM15A connected to the computer with usb, It seems to work fine.  Has anyone out there experienced this?  I'm ready to replace the CM15A. 
Title: Re: AHP & CM15A Random module turn-on
Post by: Dan Lawrence on January 16, 2011, 09:26:22 AM
I would suggest getting AHP version 3.228.   Since you have a simple system, that should work fine for you.  As to the CM15A, I got mine in July 2005 and it's still working fine.  You can get 3.228 at http://www.x10.com/support/rev_ahp.htm as a .zip file.
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 16, 2011, 11:40:13 AM
I appreciate your thoughts but I don't understand the logic in going back to an earlier version of the software.
Title: Re: AHP & CM15A Random module turn-on
Post by: Dan Lawrence on January 16, 2011, 12:57:15 PM
For a simple system (NO PLUG-INS) you don't need more than 3.228.  You want your timers to work properly.   
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 16, 2011, 01:13:51 PM
Thanks Dan.  Now I understand you!  I should have told you I have all of the plugins installed that came with my CM15A, but I'm only using AHP.   The plugins are not being utilized at this time.  Perhaps in the future I might expand the system and start using the other plugins.  Now that I have the plugins installed, can they be removed? 
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 16, 2011, 01:19:22 PM
For a simple system (NO PLUG-INS) you don't need more than 3.228.  You want your timers to work properly.   

Hi again Dan. I reported wrong, I am actually using the Smart Macro Plugin.  But that's it and it works great!

I love how the macros work and program on the CM15A.  Light-years ahead of the older AH.

Thanks, Anthony
Title: Re: AHP & CM15A Random module turn-on
Post by: Tuicemen on January 16, 2011, 01:27:31 PM
PLCGuru
You should ugrade to version 3.304 (http://www.x10.com/support/support_soft1.htm) it is a better version then 3.301.
 >!
Title: Re: AHP & CM15A Random module turn-on
Post by: Noam on January 16, 2011, 01:47:09 PM
For a simple system (NO PLUG-INS) you don't need more than 3.228.  You want your timers to work properly.   

Dan -
I thought you were able to get a stable system with later versions, after you did a complete uninstall and reinstall a little while back.
Did your system go south again?
Title: Re: AHP & CM15A Random module turn-on
Post by: Dan Lawrence on January 16, 2011, 07:42:20 PM
My system is running fine.  I did go back to 3.296 and as of today, all timers run as established.   I do not use any plug-ins, my X10 system does not need them.
Title: Re: AHP & CM15A Random module turn-on
Post by: beelocks on January 16, 2011, 08:11:13 PM
OP states that the CM15A is not connected to a computer.

Does the version of the software change the way the interface works when it is operating in stand-alone mode?  :'
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 16, 2011, 08:52:46 PM
Hey Guys, please don't hijack my thread.  I did the upgrade to 3.304 a few hours ago and again I find I have a module turning on at random.  In my activity monitor, which I am not 100% used to yet, I see this event described as "Transmit" and it's module number.  It didn't "Receive RF"  Anyone out here have any thoughts on this?
Title: Re: AHP & CM15A Random module turn-on
Post by: Tuicemen on January 17, 2011, 10:56:52 AM
Is the recycle bin in AHP empty?
purge macros
Clear your interface
empty the recycle bin
then update the interface.
Sometimes old macros & timers don't get cleared and continue to fire.
It has also been noticed that old deleted timers macros that are still in the recycle bin continue to work.
 >!
OP states that the CM15A is not connected to a computer.

Does the version of the software change the way the interface works when it is operating in stand-alone mode?  :'
Possibly, X10 added options for softstart modules.
as well as some other fixes.
Title: Re: AHP & CM15A Random module turn-on
Post by: Brian H on January 17, 2011, 11:29:26 AM
Separate section for older Lamp Modules and the new soft start Lamp Modules was added.
http://www.x10.com/support/rev_ahp.htm
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 17, 2011, 01:26:15 PM
Is the recycle bin in AHP empty?
purge macros
Clear your interface
empty the recycle bin
then update the interface.
Sometimes old macros & timers don't get cleared and continue to fire.
It has also been noticed that old deleted timers macros that are still in the recycle bin continue to work.
 >!
OP states that the CM15A is not connected to a computer.

Does the version of the software change the way the interface works when it is operating in stand-alone mode?  :'
Possibly, X10 added options for softstart modules.
as well as some other fixes.

Thanks Tuiceman, I will check the recycle bin as soon as I get home.   One bit of info you might find interesting, one of the modules that turns on by itself has no timer programmed into it.   It's a module in the system that, at this time, has no timer or macro associated with it.   

Title: Re: AHP & CM15A Random module turn-on
Post by: Noam on January 17, 2011, 03:07:29 PM
Have you tried changing the Unit code of that module, and perhaps setting a different one to that code, and see if the randomness follows the module or the unit code?

There is a somewhat common issue with the wall swtiches, which are prone to random turn-ons from electrical noise.
I ended up replacing all of mine with switches from Smarthome, instead.
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 17, 2011, 04:22:51 PM
Hi Noam.  No I haven't tried changing the unit code of any of the modules.  Mainly because all of my modules worked 100% with the CM11 for over 8 years.  Never had a problem with any of them.  As soon as I upgraded to the CM15A I'm waking up to various lights on in the house.  Nothing ever turns off when it's not supposed to - just random turn-on.   This only happens when the CM15A is running stand alone.  If I have it plugged into my computer while monitoring activity, it behaves itself, go figure! lol

My ideal scenario is to have it stand alone and set and forget it.   With the CM11, I could leave it for almost a year without maintenance.  It had a few programming quirks, but I managed to make it work.   I'd go back to it but I like the CM15A's macro capability better than the CM11, so I'd really like to tame this one. 
Title: Re: AHP & CM15A Random module turn-on
Post by: lviper on January 17, 2011, 04:33:02 PM
I've been following this thread with great interest. However, this last reply got me thinking. You mentioned it all works when the cm15a is connected to your computer but it doesn't work when it isn't connected. Just a thought, is it possible any of the macros or timers are set to run on the pc only?

Not sure as I'm still very green to this stuff, but that is the question that came to mind.
Title: Re: AHP & CM15A Random module turn-on
Post by: Tuicemen on January 17, 2011, 04:35:45 PM
PLCGuru
When you upgraded to AHP and the cm15a did you use the import function in AHP to import your CM11 settings?
For some reason users have complained that this feature never imported everything correctly and experianced many of the same issues you are seeing.
Once they rebuilt from scratch their complete setup, everything worked fine.
Now how complexed each users setups were I have no Idea as some users stated this function worked fine for them.
 >!
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 17, 2011, 07:32:05 PM
Hi Tuicemen, earlier I was asked to check the recycle bin, it's empty.  I don't know how to make programs run on the PC only.  I'm opening the file, making changes and, saving and downloading the data to the CM15A.  When I upgraded from the CM11 to the CM15A, I built the program from scratch.  I did not import any files or data. I figured writing the program was a better way to learn and it wasn't that difficult.  As I previously mentioned, I only have 9 modules, two outdoor motion detectors and four macros in the program.  Not much memory used up. 
Title: Re: AHP & CM15A Random module turn-on
Post by: Tuicemen on January 18, 2011, 08:30:39 AM
When you edit your macros at the bottom under the text box there are 2 radio buttons one says "Store in interface" the other says "Run fromPC".
You want the one that says store in interface colored.
My note book won't allow a print screen or I'd attach a pic but I'm sure someone else can do that if needed!
If the program won't allow you to to change it to store in interface then that macro Must be run from the PC.
 >!
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 18, 2011, 01:24:51 PM
Yes, I went looking for it this morning and found the two buttons.  I am storing both my macros in the interface.  I have new progress to report.  I think I might have found the problem.  I've never seen this before but it looks like the issue is not the CM15A but related to an aging CF lamp.  It's a 9 watt lamp that is 4 years old.  It's also the lamp is turning on at random more than the others.   This lamp is plugged into an appliance module and to boot, I have a filter on the lamp.  This morning, while I had the CM15A memory wiped clean and unplugged, (it was sitting on my table) this lamp turned on by itself.  Puzzled, I then plugged in a RR501 and with a palm transmitter, I turned the lamp off.  5 seconds later it turned itself back on.  After I repeated this 4 to 5 times, I figured it was time to replace the CF and screw in a 40 watt incandescent lamp.  The 40 w lamp works fine.  I'm going to leave in the 40 watt lamp and RR501 for now and monitor the system for the next few days.  If I see that it my system is stable with the RR501 and 40W lamp, I'll feel confident in reinstalling the CM15A.   It's funny how this CF started to act up right after I upgraded the to the CM15A.  Fooled me!  ;D

Ill get back in a few days - hopefully with a favourable report that all is well with my CM15A. >!
Title: Re: AHP & CM15A Random module turn-on
Post by: Tuicemen on January 18, 2011, 03:12:58 PM
CFLs have been known to get noisy with age! ::) :'
Title: Re: AHP & CM15A Random module turn-on
Post by: Noam on January 18, 2011, 04:20:45 PM
Fluorescent lights, (including CFL's) and appliance modules don't always get along. The current sensing circuit in them has a tendency to get confused by the circuitry in the light.
The "workaround" for this is to plug a power strip, or a multi-tap into the appliance module, and plug a night-light (incandescent) into one of the outlets. The filament in the bulb creates enough resistance to overcome this quirk.

There is a fix out there (at least for older appliance modules), but it involves cutting a wire inside the module (which you do at your own risk, of course).
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 18, 2011, 04:34:54 PM
Yes, I agree it was probably the age of the CFL along with the current sensing.  This is the only CFL I have on an appliance module.  I think I will get a new CFL, disassemble the module and remove the current sensing.  I have the instructions somewhere around here.   Funny how the coincidence of a faulty CFL and the changing of my controller had me messed up.  I feel a bit embarrassed.  I should have caught it before putting all you folks to so much head scratching!  The upside is that my CM15A seems to be working.  Thanks to all for jumping in to help.  I appreciate it. >!
Title: Re: AHP & CM15A Random module turn-on
Post by: dave w on January 18, 2011, 06:08:51 PM
Yes, I agree it was probably the age of the CFL along with the current sensing. 

FWIW The world famous "Brian H Testing Laboratory" has determined the new generation of Appliance Modules do not have "Local Control". They do still have a very small current running through the load in order to sense the relay position.

The Brian H Testing Laboratories has issued a new detailed analysis of Local Control feature for the new design Appliance Modules and is in the process of revising the initial test results.  :D
Title: Re: AHP & CM15A Random module turn-on
Post by: Brian H on January 18, 2011, 06:53:48 PM
My tests where flawed.  B:(
My normal test is turn Off a module. Unscrew and then tighten the bulb in the test socket of my test rig. They do stay Off.
Today I added a toggle switch between the module and the light socket. It did turn On when I cycled the switch.   :-[
I don't know if it was noise. As trying the bulb thing still results in it staying Off. While older modules will go On with the bulb trick.
Tried three CFL friendly one with the same results.
Title: Re: AHP & CM15A Random module turn-on
Post by: PLCGuru on January 20, 2011, 06:52:09 AM
It's official - problem solved.  2 days now without random module turn on.  My CM15A is running like a top!  The only question remaining is why did my system behave itself when the CM15A was connected to the computer via USB?  I guess we will never know. 

Thanks to all that helped. I really appreciated it..... I guess this thread can be closed.  >!

Title: Re: AHP & CM15A Random module turn-on
Post by: leroy.martin on January 21, 2016, 05:22:11 PM
I have the same problem of lights turning on randomly, especially when it's dark outside.  My smart meter is a Landis & Gyr which was installed when I put PV solar on my shop about 6 years ago.  The problem has gotten appreciable worse and now it's every night.  I even removed my controller and took it to a different location. Is there any way to correct this problem.
Title: Re: AHP & CM15A Random module turn-on
Post by: dave w on January 21, 2016, 08:40:40 PM
Little more information:
Is it always the same lights? What kind of controller do you have?
If it is always the same lights, is it the same time, or is that random also?
If only one or two lights and they are incandescent, make sure the bulb is tight in the socket. (Yeah it sounds funny, but I have had bulbs "walk" themselves loose in the socket and the loose connection would activate the "Local control" feature.)
Title: Re: AHP & CM15A Random module turn-on
Post by: JeffVolp on January 22, 2016, 10:36:54 AM
My smart meter is a Landis & Gyr which was installed when I put PV solar on my shop about 6 years ago.

Some of our customers have had severe problems with powerline noise from solar system inverters, and had to isolate them with the big X10 XPF in-line filters.

Jeff