Hi, I need help for installation ws13a in brazil... The my actual installation don't have three wires. In manual i not understend the wires for lamp. I did a drawing, i think it easier to understend.
(https://lh3.googleusercontent.com/_xXciK8gsm9I/TW0Wd3Kek8I/AAAAAAAAABQ/P492YydmhEs/s576/ws13a.jpg)
What wires i have to conect in LINE, NEUTRAL and LOAD?
What wires go to lamp?
Tks all
-
Your power is 120 volts 60 cycles correct?
I understand some of Brazil is 220 volts only. If the power around the world web site is correct.
The WS13A is strictly 120 volts.
Your diagram has one error in it.
The Blue wire from the light bulb to the connection on the switch. Is not the neutral. It is the load.
If you only have the two wires in the switch box. You need to add a neutral from somewhere or you can not use a WS13A.
So in your diagram as it is now.
The Red in the switch box is the Line
The Blue in the switch box to the light bulb is the load.
Neutral wire is missing and has to be added to the switch box..
-
My Power is 120 volts.
I understand, so, what is neutral? is blue wire the wall socket?
if yes, can be conected equal this diagram:
(https://lh6.googleusercontent.com/_xXciK8gsm9I/TW0c_O545gI/AAAAAAAAABk/MpEi8E1Yaw0/ws13a2.jpg)
tks
-
The WS13A needs the GREEN wire in your diagram.
-
I understand, i go to test.... if my house not fire i post the result... rofl
tks
-
Dan; The Green Ground safety wire is not required for the WS13A to work.
It is for safety but not to work correctly.
-
Thanks for the "heads up".