I have the same problem and read this post so I tried your suggestion and it didnt work, but then I tried the Universal module UM506 and I can turn the lights on and off Manually from th AH PRO console or download to the interface. I tested theis a couple times and it worked...now I'm putting it into production test for tonight....Thanks for the idea and I'll let you know if it works.
cencinio,
The UM506 interface is similar to an appliance module - it sends simple on/off commands (no bright/dim).
Are you using a WS12 wall switch (dimmer)?
If so, please try the following:
- Re-identify you unit as a LM14a
- Move the bright/dim slider to ~50%
If the above works, your unit is compatible with the LM14a interface (if it's a soft start unit it should be).
After making the above change, you may need to "edit" the macro that uses the switch before AHP uses the proper codes in the macro. Simply edit the macro, change the dim setting, and then save to the interface.
When you activate the macro your should see something similar to the following in the Activity Monitor -
Macro A2 extended code XX 31
If you do not, the macro hasn't recognized the switch change.
I have also recently learned that the LM14a interface will not function properly at address A1 if you are using AHP 3.228. This appears to be a bug. Please do not use A1 for soft start modules.