Please login or register.

Login with username, password and session length

Author Topic: UM506 (Universal Module) and Trine Electric Strike  (Read 3288 times)

luis84

  • Jr. Member
  • **
  • Helpful Post Rating: 0
  • Posts: 21
UM506 (Universal Module) and Trine Electric Strike
« on: July 10, 2012, 04:58:02 PM »

Hello Everyone,

I would really appreciate the help of any experts.  I own a UM 506 module (now discontinued).  It outputs an electrical signal from two contacts, 5A / 24 VDC

I also own a Trine 3024 Electric Strike, which, requires 24 DC @ .240 Amps / 100 OHMS

I tried to connect the Trine to the UM506, I turn on the UM 506 and the buzzer sounds but the trine strike does not activate.  I have it wires with one wire from the trine to each contact on the UM 506, I am thinking maybe I wired it wrong.

Could anyone chime in, any suggestions would be great! I was really hoping to use this for an internal door, I am bummed out now.  I am really hoping it's just a simple mistake :-(

This is the UM506: http://www.x10.com/products/x10_um506.htm
This is the Trine 3024: http://www.lock-depot.com/servlet/the-6141/Trine,-dsh-,Parts-cln-,3024/Detail

Here is a picture of my setup:
Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: UM506 (Universal Module) and Trine Electric Strike
« Reply #1 on: July 10, 2012, 05:54:41 PM »

The attached photo didn't show correctly.

The UM506 is like a remote controlled switch. It does not supply any voltage on the screws. The 24VDC 5A is the maximum power it can safely switch.

You need an external power supply to provide the power and use the UM506 to switch the it the 24 volts On and Off.


Power Supply             Lock Strike                        UM506
*----------------------*     *---------------------*   *
*-----------------------------------------------------|

« Last Edit: July 10, 2012, 06:10:35 PM by Brian H »
Logged

dave w

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 139
  • Posts: 6116
Re: UM506 (Universal Module) and Trine Electric Strike
« Reply #2 on: July 10, 2012, 07:59:10 PM »

You must have lost your instructions. Hope this helps.
http://software.x10.com/pub/manuals/um506-is.pdf
« Last Edit: July 10, 2012, 08:01:19 PM by dave w »
Logged
"This aftershave makes me look fat"

luis84

  • Jr. Member
  • **
  • Helpful Post Rating: 0
  • Posts: 21
Re: UM506 (Universal Module) and Trine Electric Strike
« Reply #3 on: July 11, 2012, 06:06:30 PM »

Hello,

My module had no instructions (due to age) and also ... I am new to this module.  So thank you both very much.

So would it be like this

UM506 - Two terminals
24vdc transformer

I will connect one wire of the transformer + 1 wire of the electric strike to one terminal, the other wire of the electric strike to the other terminal.  When activate, it will bridge the two terminals and complete circuit - thus activate strike.

Is that correct?

Thank you
Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: UM506 (Universal Module) and Trine Electric Strike
« Reply #4 on: July 11, 2012, 06:16:10 PM »

One terminal of the UM506 to one terminal of the 24 volt supply.
The other terminal of the UM506 to one of the strikes connection.
Wire from other terminal of the 24 volt supply to the other terminal of the strike.
Logged

luis84

  • Jr. Member
  • **
  • Helpful Post Rating: 0
  • Posts: 21
Re: UM506 (Universal Module) and Trine Electric Strike
« Reply #5 on: July 28, 2012, 01:27:25 AM »

Hello - Worked like a charm. Thanks.
Logged
 

X10.com | About X10 | X10 Security Systems | Cameras| Package Deals
© Copyright 2014-2016 X10.com All rights reserved.