Mini controller question
« on: February 28, 2017, 11:34:10 PM »

Hi,
In my home there is 220 VAC coming in to the breaker box and converted to 110 VAC on two legs. If I plug X10 into leg 1, it will not communicate with X10 modules plugged into Leg 2. There are devices that plug into 220 VAC outlet and connect the two phases. Have you had any experience with this?  The other fix would be to add another mini controller.
Logged

HA Dave

  • Hero Member
  • *****
  • Helpful Post Rating: 175
  • Posts: 7127
Re: Mini controller question
« Reply #1 on: February 28, 2017, 11:52:20 PM »

I user a dryer plug phase coupler on my setup. They may not be as easy to find as they once were.
Logged
Home Automation is an always changing technology

Leayer

  • Jr. Member
  • **
  • Helpful Post Rating: 0
  • Posts: 17
Re: Mini controller question
« Reply #2 on: March 01, 2017, 03:54:38 AM »

Thanks for the advice. This phase coupler is unavailable but still looking.  See this capacitor and let me know what you think! Thanks.

http://www.ebay.com/itm/X10-Phase-Coupler-Signal-Bridge-Stops-Most-Intermittent-X10-Problems-/161908395202?hash=item25b27e0cc2:g:F94AAMXQhpdRvhWP

Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: Mini controller question
« Reply #3 on: March 01, 2017, 06:22:34 AM »

Thanks for the advice. This phase coupler is unavailable but still looking.  See this capacitor and let me know what you think! Thanks.

http://www.ebay.com/itm/X10-Phase-Coupler-Signal-Bridge-Stops-Most-Intermittent-X10-Problems-/161908395202?hash=item25b27e0cc2:g:F94AAMXQhpdRvhWP

Do you need the 3 or 4 prong version of the Smarthome Passive Dryer Coupler? The linked manual covered both models.

There was also a Smarthome Coupler/Repeater. In both 3 and 4 prong versions.
http://cache-m2.smarthome.com/manuals/4826a.pdf

Not the best idea. That capacitors does not look like one designed or rated for across AC power use.
We have seen the plain capacitors across the two incoming power lines. Burn up or just fail.

They do make passive phase couplers that are made to couple X10 and Insteon signals across the power lines. Both of these
could be found on some independent dealers for less. The Smarthome one says Insteon but it also does X10.
https://www.x10.com/x10-pro/specialty-devices/couplers-repeaters/xpcp-ratio-passive-coupler.html
http://www.smarthome.com/signalinc-insteon-2406h-phase-coupler-hardwired.html

You can also get X10 power line repeaters. They take the signal at the breaker box and resent it at full strength back on the other line. X10Pro has the XPCR. JVDigital has the best line in the business.
https://www.x10.com/x10-pro/specialty-devices/couplers-repeaters/xpcr-coupler-repeater-amplifier.html
http://jvde.us/index.htm
« Last Edit: March 01, 2017, 07:17:45 AM by Brian H »
Logged

JeffVolp

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 122
  • Posts: 2299
    • XTB Home Page
Re: Mini controller question
« Reply #4 on: March 01, 2017, 08:53:16 AM »

See this capacitor and let me know what you think!

http://www.ebay.com/itm/X10-Phase-Coupler-Signal-Bridge-Stops-Most-Intermittent-X10-Problems-/161908395202?hash=item25b27e0cc2:g:F94AAMXQhpdRvhWP

While better than nothing, the capacitor does not "PROVIDE OPTIMUM COUPLING OF X10 SIGNALS".  It has a capacitive reactance of 13 ohms at the X10 carrier frequency.  A series-resonant tuned circuit provides much better coupling.  And as Brian said, even though it is rated for 630VDC, that capacitor is not marked as X2 rated for across-line operation.

For a good passive coupler, look for the X10 XPCP.  You might also want to read my troubleshooting guide on couplers:

    http://jvde.us/x10/x10_couplers.pdf

Jeff
Logged
X-10 automation since the BSR days

bkenobi

  • PI Expert
  • Hero Member
  • ******
  • Helpful Post Rating: 24
  • Posts: 2082
Re: Mini controller question
« Reply #5 on: March 01, 2017, 10:56:37 AM »

I used the passive phase coupler (forget the model number) and it worked well.  I had issues with reliability so I decided to upgrade to a coupler-repeater.  I decided to opt for the XTB-IIR but the X10 version might have worked ok too.  The one I have (many others do too) is not the cheapest option, but it's by far the best thing I've done for signal reliability.
 

X10.com | About X10 | X10 Security Systems | Cameras| Package Deals
© Copyright 2014-2016 X10.com All rights reserved.