Author Topic: XPS4 Installation issue --Neutral?  (Read 2288 times)

patches

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 2
XPS4 Installation issue --Neutral?
« on: May 07, 2017, 02:28:15 PM »

Attempting to install an XPS4 to control a dock light in a back wired(no neutral) situation.  However; in the same 2 gang box is a switch for a porch light with a neutral, which I jumpered from.  Upon installation, it immediately tripped the GFI.  After fussing a bit, I think the problem is that the porch light comes from a 200 A. house panel, and the dock light is out of a 100A outside panel.  So the neutral terminates in a different panel than my dock light power.

Sound like I am SOL?  Or am I missing something else.  Any thoughts appreciated.

Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: XPS4 Installation issue --Neutral?
« Reply #1 on: May 07, 2017, 03:02:16 PM »

Are you sure it is a Neutral?

If the White Wire is connected to one of the porch light switch's terminal. Along with a Black wire on the other terminal.
You have a switch loop.

Another indication of a switch loop would be a black piece of tape or black marker on the white wire that you think is a Neutral.

In a switch loop. The white wire {should have a black indicator on it} is actually the Line from the fixtures electrical box and the black is the load to the light.

If the white wire you used is in a bundle of white wires then it maybe a neutral but on the other breaker box. As you thought.
« Last Edit: May 07, 2017, 03:05:33 PM by Brian H »
Logged

JeffVolp

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 122
  • Posts: 2299
    • XTB Home Page
Re: XPS4 Installation issue --Neutral?
« Reply #2 on: May 07, 2017, 03:38:03 PM »

Upon installation, it immediately tripped the GFI.  After fussing a bit, I think the problem is that the porch light comes from a 200 A. house panel, and the dock light is out of a 100A outside panel.  So the neutral terminates in a different panel than my dock light power.

Unless the neutral return goes back to the same GFI that sources power for the light, the GFI will see an imbalance and immediately trip.

Jeff
Logged
X-10 automation since the BSR days

patches

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 2
Re: XPS4 Installation issue --Neutral?
« Reply #3 on: May 07, 2017, 04:25:20 PM »

Thanks Jeff,

That's what I thought the problem was.  Now I guess my next option is an XPFM in the panel box.



« Last Edit: May 07, 2017, 04:27:23 PM by patches »