Author Topic: 20A rated light switch on 15A breaker  (Read 10379 times)

jeff

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 1
20A rated light switch on 15A breaker
« on: December 15, 2005, 02:33:37 PM »

Does anyone know if you can connect the
XPS3 20A wall switch to a 15A breaker. Will
this cause a problem. My light switch is
only a 15A light switch. The lights will
only draw about 75Watts total.
Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: 20A rated light switch on 15A breaker
« Reply #1 on: December 15, 2005, 04:30:11 PM »

Yes no problem. The switch can handle 20
amps and the breaker will trip over 15 amps.
So the switch can take a higher current than
the breaker.
Logged

gil shultz

  • Sr. Member
  • ****
  • Helpful Post Rating: 4
  • Posts: 139
Re: 20A rated light switch on 15A breaker
« Reply #2 on: June 13, 2007, 05:03:42 AM »

This will not cause any problems and would be considered derating or conservative design.

Remember the breaker or fuse is designed to protect the wire, not the load.  By putting a higher rated device then the main breaker is no problem, going the other way could possibly be a problem depending on conditions at the time of the fault.

Gil Shultz
Logged
 