Please login or register.

Login with username, password and session length

Author Topic: [HELP] GE Zoneline Heatpump BLOCKS X-10 Signal (When Compressor Is Running)...  (Read 5478 times)

doughohl

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 1

I have three General Electric Zoneline thru wall heatpumps with 4,5 KW heating elements each. When these units are in the heatpump mode the compressors block the x-10 signals. The circuit size is 40 a at 240v. I have not been able to find an in-line filter to install on these units to keep them from blocking the signals. Any suggestions?


[TTA Edit: Re-worded title in an attempt to attract someone with an answer and/or suggestion.]
« Last Edit: March 05, 2007, 01:04:22 PM by TakeTheActive »
Logged

JeffVolp

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 122
  • Posts: 2299
    • XTB Home Page

I am not familiar with that unit.  Even though it is a 240V unit, it might still have bypass capacitors sucking the X10 signal to ground. I am not aware of any filters that will handle that much current.  The only suggestions I have are to increase your X10 signal levels by either moving your X10 transmitter near the main distribution panel, or adding a XTB to boost the output of the transmitter.

Jeff
Logged
X-10 automation since the BSR days
 

X10.com | About X10 | X10 Security Systems | Cameras| Package Deals
© Copyright 2014-2016 X10.com All rights reserved.