Yes - 3.318
House code L disabled - Was set to Auto; A, B, C, D, H, L & P were all checked. I tried selecting "None" as well as "Specific" with everything checked and updated between tries with the same result
I deleted my existing lamp modules and added new ones from the Older Lamps(no SoftStart) menu and set them to On in the macro.
Same results. I can trigger from AHP but not the CR12A.
When triggering from AHP, I get a visual AND audible signal. But when I trigger from the CR12A, I only get a visual signal ("run macro" flashes)
It seems odd that the CR12A works for controlling the individual lamps but not the macros.
With Hardware configuration set to None, I created a new macro to turn on L2 with trigger L3
"SimpleTest" Macro settings are
Trigger = L3 On
Lamp L2= On
L2 On from the CRL2A
Receive RF L2 On
Receive L2 (Lamp 2)
Receive L On (Lamp 2)
Result= Lamp turns on (PASS)
Trigger Macro from AHP
Transmit L Bright 100% (Lamp 2)
Result= Lamp turns on (PASS)
Trigger from Cr12A L3 On
Receive RF L3 On
Receive L3 (SimpleTest)
Receive L On (SimpleTest)
Result= Lamp stays off (FAIL)