Please login or register.

Login with username, password and session length

Author Topic: Existing X10 Installation PLC Not Reaching All New Addition Rooms  (Read 3566 times)

esevin

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 1

I have an old (maybe the original) X-10 controller with 3 lamp modules that worked fine until we added several new rooms to the house. Now there is a preferential location for the controller and modules depending in what section/room of the house they are installed. Some rooms in the old house have original, non-grounded- wiring; others have grounded outlets as do all of the new rooms. For example, the controller located in one of the new rooms successfully operates modules in another new room and some of the old rooms but not in other old rooms; the same situation results when the controller is located in an old, non-grounded, room. Is there any fix to this?
Logged

Puck

  • Advanced Member
  • Hero Member
  • ******
  • Helpful Post Rating: 171
  • Posts: 1799
Re: Existing X10 Installation PLC Not Reaching All New Addition Rooms
« Reply #1 on: December 08, 2006, 01:58:26 PM »

esevin: X10 signals do not require ground wire, so that will not be your problem. Most likely you have a phase / noise / signal sucker issue.

Check out the following posts:

TTA's: MAP / MEASURE / CORRECT

How to Map your Electrical Circuits

Also do an Advanced Search on phase / line noise / signal sucker.
Logged

HA Dave

  • Hero Member
  • *****
  • Helpful Post Rating: 175
  • Posts: 7127
Re: Existing X10 Installation PLC Not Reaching All New Addition Rooms
« Reply #2 on: December 08, 2006, 06:17:53 PM »


How to Map your Electrical Circuits


Puck should have mentioned that this is particularly well written piece (as are the others) that will likely give you real insight to your problem!
Logged
Home Automation is an always changing technology
 

X10.com | About X10 | X10 Security Systems | Cameras| Package Deals
© Copyright 2014-2016 X10.com All rights reserved.