Please login or register.

Login with username, password and session length
Pages: [1] 2

Author Topic: AHP not updating when switches are turned on.  (Read 8687 times)

dbemowsk

  • Hero Member
  • *****
  • Helpful Post Rating: 21
  • Posts: 428
    • PHP Web Scripting
AHP not updating when switches are turned on.
« on: December 27, 2009, 09:23:19 PM »

I have some dimming (WS12A) and some relay type (XPS3-IW) switches installed.  These switches respond to commands sent from remotes or from AHP directly and turn on and off accordingly.  When turned on from AHP or a remote, AHP shows that the device is on or off as it should.  My problem comes in  when I turn these switches on from the switch directly.  When I do this, AHP does not indicate that the switch is on.  Is this the way these switches are designed to work?  Do I need to upgrade to a different kind of switch that will update AHP when the switch is controlled directly? 

I don't see the point of these if they will not update the software.  I am writing a PHP database driven application using the SDK that will allow me to check the status of lights and other things in my house from anywhere.  The application currently will show me the layout of my house with lighting and appliances that are on or off.  See my alpha version here http://66.190.8.188:8088/index.php.  The issue I have with this is that the SDK only shows me what AHP knows to be on or off.  If my wife decides to go turn on the light above the sink using the switch, it does not notify AHP that the light is on, thus my application will not show this.

Any help on this is appreciated.

Dan Bemowski
Logged
Dan Bemowski
Owner of PHP Web Scripting LLC
Programmer of RemoteWatch X10
User of any X10 products I can get my hands on.

beelocks

  • Hero Member
  • *****
  • Helpful Post Rating: 9
  • Posts: 250
Re: AHP not updating when switches are turned on.
« Reply #1 on: December 27, 2009, 10:42:17 PM »

X10 switches are one-way devices. They receive a signal and act on it. What they cannot do is report back to let AHP know that they have been turned on manually. Someone here will almost certainly tell you the model numbers of the two-way modules which you'll need for your project.
Logged
Although my explanations may not be exactly clear, I do hope for slightly less cloudy.

Dan Lawrence

  • Hero Member
  • *****
  • Helpful Post Rating: 68
  • Posts: 3991
Re: AHP not updating when switches are turned on.
« Reply #2 on: December 27, 2009, 10:46:09 PM »

That's the way AHP is written.  I just walked into the bedroom and turned the lights on by pushing the button on the Wall Switch module. I walked back to the computer where AHP was open.  AHP showed the wall switch as off.   Unless you use a two-way module, AHP does not show status of a module that it did not turn on.
Logged
I don't SELL this stuff... BUT I sure do ENJOY using it!!!

dbemowsk

  • Hero Member
  • *****
  • Helpful Post Rating: 21
  • Posts: 428
    • PHP Web Scripting
Re: AHP not updating when switches are turned on.
« Reply #3 on: December 27, 2009, 11:12:24 PM »

X10 switches are one-way devices. They receive a signal and act on it. What they cannot do is report back to let AHP know that they have been turned on manually. Someone here will almost certainly tell you the model numbers of the two-way modules which you'll need for your project.
I have seen some X10 stuff that claims to be 2-way, but have not tried any as of yet.  Can you suggest any switch devices/modules that will update AHP when activated manually?

Dan
Logged
Dan Bemowski
Owner of PHP Web Scripting LLC
Programmer of RemoteWatch X10
User of any X10 products I can get my hands on.

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: AHP not updating when switches are turned on.
« Reply #4 on: December 28, 2009, 06:53:34 AM »

I have not seen any X10 or X10Pro switches or modules that are two way presently being made. The LM14A Lamp and AM14A Appliance modules where discontinued. As where the X10Pro PAM21 Appliance and PLM21 Lamp Modules.

I know the Smathome Insteon Protocol switches and modules are two way and can have an X10 Address programed in to them. My earlier revision SwitchLinc relay sends an X10 on and off when locally actuated. To the Primary X10 Address I programmed in to it.

Few things with those switches.
Much more costly.
Need a real Neutral Power Connection in the switch box.
The dimmer versions handle dimming differently. They do not send the stream of bright or dim commands when the local controls are used or the Extended X10 commands used by the two way modules.
When the paddle is released it sends a %of Dim command that X10 does not understand. The dimmer switch does sent an on or off at 0% and 100% with the local paddle. So my test Insteon SwitchLinc Dimmer did register a on or off in AHP when locally toggled, but not if it was locally dimmed.

I am not sure if the latest revision Lamp and Appliance Modules in the Insteon line now send status change when local control toggles them on.

ACT use to make some two way switches but I have not seen them lately.

Since two way devices have a power line transmitter in them. They also can absorb power line signals. So if your setup was marginal but not showing communications problems. Changing to two way devices could deteriorate the setup and you may notice it.
« Last Edit: December 28, 2009, 10:51:19 AM by Brian H »
Logged

JeffVolp

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 122
  • Posts: 2299
    • XTB Home Page
Re: AHP not updating when switches are turned on.
« Reply #5 on: December 28, 2009, 10:19:59 AM »

Leviton also makes some high-end two-way X10 compatible switches, but they are about $80 a pop.  That is clearly out of the range of most people who choose to go with X10.

Jeff
Logged
X-10 automation since the BSR days

dbemowsk

  • Hero Member
  • *****
  • Helpful Post Rating: 21
  • Posts: 428
    • PHP Web Scripting
Re: AHP not updating when switches are turned on.
« Reply #6 on: December 28, 2009, 01:45:33 PM »

OK, I did some searches on the insteon line and I found their ICON series which seems to be their cheaper series of switches.  Has anyone used these?  Are they much cheaper in quality from their higher priced products?  Are they 2-way, and do the dimmers report % of dim? 

Thanks for all the great help.

Dan
Logged
Dan Bemowski
Owner of PHP Web Scripting LLC
Programmer of RemoteWatch X10
User of any X10 products I can get my hands on.

Puck

  • Advanced Member
  • Hero Member
  • ******
  • Helpful Post Rating: 171
  • Posts: 1799
Re: AHP not updating when switches are turned on.
« Reply #7 on: December 28, 2009, 02:06:36 PM »

OK, I did some searches on the insteon line and I found their ICON series which seems to be their cheaper series of switches.  Has anyone used these?  Are they much cheaper in quality from their higher priced products?  Are they 2-way, and do the dimmers report % of dim? 

Thanks for all the great help.

Dan

I have and use the ICON switches and they do report correctly in AHP. When manually pressed, they send their X10 address with ON or OFF along the power lines. I have not used the dimmer versions.

As for quality, a few of the ones I have no longer work manually (ON & OFF) after about a year. They still work with PLC signals. I have not yet had the need or desire to remove and open one to check the switches; since the failed ones are currently where I only need automated lighting.
Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: AHP not updating when switches are turned on.
« Reply #8 on: December 28, 2009, 03:32:50 PM »

Basically the Icon has less features. Like no Brightness Bargraph; no adjustable ramp rate; 30 Insteon Link database not 417; 1 year warranty; no X10 Scenes only an X10 Primary Address. Lower wattage rating for the maximum load. Single LED indicates it is Off. Goes out when turned on. LED is Amber. Insteon is bright white Bargraph and you can change the light pipes. I use dark blue or frosted myself.

Smarthome recently revised both the Icon and Insteon switches.
I have a below Revision 5 {where redesign was implemented} Icon Dimmer switch.
Added an X10 address and used for test only Smarthome Manager Essentials with 1132CU interface. To watch the switches operation.
It sends a %of dim when not set to 0% or 100%. At 0% it sends the X10 off and at 100% the X10 On.
I doubt the revisions above 5.0 handle X10 any differently than the older ones.
There maybe a few other differences in above 5.0 that I am not aware of.

Also where you have your WS12A switches. You would need a Neutral Power Wire in the switch box for the Icon or Insteon switches to work.
« Last Edit: December 28, 2009, 04:30:35 PM by Brian H »
Logged

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: AHP not updating when switches are turned on.
« Reply #9 on: December 28, 2009, 03:36:09 PM »

Puck; There was a known problem with the earlier tact switches in both the Icon and Insteon switches. Smarthome extended coverage for the switches in a known manufacturered time frame. Replacements where being provided as warranty even if the normal 2 year for Insteon or 1 year for Icons was past.
The latest ones have a updated tact switch.
Logged

dbemowsk

  • Hero Member
  • *****
  • Helpful Post Rating: 21
  • Posts: 428
    • PHP Web Scripting
Re: AHP not updating when switches are turned on.
« Reply #10 on: December 28, 2009, 05:58:52 PM »

Is it true that X10 PRO devices can be polled for status?  I know that they would not be able to automatically tell AHP that they were turned on when manually activated, but if I could create a macro that would run every so often  to poll the status of a device and if polling shows that for example B5 is on, then send a B5 ON command to update AHP with it's status.  If this is possible, I can keep my current X10 PRO switches and go with more Insteon devices in the future.

As always, I appreciate all the input given from the brain trust within this forum.

Dan
Logged
Dan Bemowski
Owner of PHP Web Scripting LLC
Programmer of RemoteWatch X10
User of any X10 products I can get my hands on.

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: AHP not updating when switches are turned on.
« Reply #11 on: December 28, 2009, 06:26:28 PM »

I believe the X10Pro modules are also one way. So there would be no way to get an answer from a Status Request.
If you XPS3-IW was two way it would report a local change in state.
I have one and will double check it.
Logged

dbemowsk

  • Hero Member
  • *****
  • Helpful Post Rating: 21
  • Posts: 428
    • PHP Web Scripting
Re: AHP not updating when switches are turned on.
« Reply #12 on: December 28, 2009, 06:44:03 PM »

What command do I use to check status?  I have one installed and can test it in a few seconds if I know what I have to do.

Dan
Logged
Dan Bemowski
Owner of PHP Web Scripting LLC
Programmer of RemoteWatch X10
User of any X10 products I can get my hands on.

Brian H

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 305
  • Posts: 13295
Re: AHP not updating when switches are turned on.
« Reply #13 on: December 28, 2009, 07:11:59 PM »

I don't use AHP much these days.
I believe it is a poll to the devices address for its status.

In my Smarthome Essentials with the 1132CU interface. A status request to my X10 RR501 that is two way got me an off responce.
The XPS3-IW got no reply.

I also tried it in AHP calling it a two way module. Again no action with a poll to the devices address.
Logged

Dan Lawrence

  • Hero Member
  • *****
  • Helpful Post Rating: 68
  • Posts: 3991
Re: AHP not updating when switches are turned on.
« Reply #14 on: December 28, 2009, 07:23:34 PM »

The only thing you can poll in AHP is the RR501 Transceiver which has a Poll button, but you never get a reply.  It's most likely a tiny bug in AHP's programming.
Logged
I don't SELL this stuff... BUT I sure do ENJOY using it!!!
Pages: [1] 2
 

X10.com | About X10 | X10 Security Systems | Cameras| Package Deals
© Copyright 2014-2016 X10.com All rights reserved.