Author Topic: x-10 Light Switches and Appliance Modules work inconsistently...FIXED!!  (Read 3411 times)

rb1204

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 2

UPDATE:  decided to map every outlet/light in the house.  Found an obscure outlet tied to problem circuit, with a recharging flashlight connected.  Removed the recharger, things started working!!  Thanks to all for your help.

My system :  two light switches, two appliance modules, one timer (looks like an alarm clock).  System worked fine for 10 years - then various devices slowly started working inconsistently.  I've turned all the breakers off/on, until I found the problem circuit.  It was the circuit feeding power to the kids' bedroom.  I unplugged everything feeding this circuit, unwired the ceiling fan/lights, and unwired the closet fluorescent lights.  When the power is on to this circuit, with nothing connected/wired, the x-10 modules work inconsistently.  When the power is off, everything works fine.  I have no bridges/couplers/filters.

To verify that nothing else is on this circuit - I did a connectivity test across ground and the hot wire (disconnected from the breaker) - there was no connectivity.  Also hooked up my ammeter in series with the hot wire and the breaker - no amps were being drawn.  (I guess something could still be connected, not turned on, but still generating 'noise', but have yet to find it...).   When things work with breaker off, one appliance module is on the 'A' side, one appliance module and the timer is on the 'B' side - all work fine with breaker to problem circuit off.

Any thoughts on what could be causing this?

Thanks!!
« Last Edit: December 19, 2011, 11:43:45 AM by rb1204 »
Logged

dave w

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 139
  • Posts: 6116

When the power is on to this circuit, with nothing connected/wired, the x-10 modules work inconsistently.  When the power is off, everything works fine.  I have no bridges/couplers/filters.

To verify that nothing else is on this circuit - I did a connectivity test across ground and the hot wire (disconnected from the breaker) - there was no connectivity.  Also hooked up my ammeter in series with the hot wire and the breaker - no amps were being drawn.  (I guess something could still be connected, not turned on, but still generating 'noise', but have yet to find it...).   When things work with breaker off, one appliance module is on the 'A' side, one appliance module and the timer is on the 'B' side - all work fine with breaker to problem circuit off.

Any thoughts on what could be causing this?

Thanks!!
Yes, something you have yet to find. Obviously something is still on the circuit besides the kids room. How low does your amp meter go? A switching power supply may only draw a few millamp and may have no detectable resistance when unpowered, if capacitivly coupled. Also the fact that it came on slowly might indicate a CFL bulb going bad.

http://jvde.us/x10_troubleshooting.htm

Easiest fix may be to install a XPCR repeater. Don't know if you can still find a 20 buck unit on Ebay anymore, though.
Logged
"This aftershave makes me look fat"

Noam

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 51
  • Posts: 2818

When things work with breaker off, one appliance module is on the 'A' side, one appliance module and the timer is on the 'B' side - all work fine with breaker to problem circuit off.

Which phase (A or B) is the problem circuit on?
Are you sure that the modules and the timer are on opposite phases? Most modern breaker boxes alternate horizontal rows (for a breaker box mounted vertically), so that every other breaker when moving down the box is on an alternating phase. The two breakers across from each other generally are on the same phase.

That's the way It's been with every box I've ever looked at. It is possible that some boxes might be wired differently, of course.

One other thing (which Dave touched on) is that the circuit might not be feeding ONLY the kids' bedroom. I've seen this a lot, especially in my house (which was built in 1964).

It is also possible that the breaker itself might be the problem.
You said you tested the circuit with the "hot" wire disconnected from the breaker, and couldn't find a load on it.
Did you test with the circuit disconnected from the breaker, but the breaker turned on?
Logged

rb1204

  • Newbie
  • Helpful Post Rating: 0
  • Posts: 2

All - thanks for the help!!

The timer, one appliance module, and a light switch is on phase B.  The problem circuit, and one appliance module, is on phase A.  As a test, I moved the problem breaker to phase B, and had the same results.  The results are consistent - when the breaker is off, all appliance modules and light switch work, when the breaker is on, all work inconsistently (sometimes on/off commands work, most often they do not...).  I also ran these tests with all 220 breakers tripped (to try to eliminate any cross phase coupling by an appliance) - all results were the same.

Ammeter goes pretty low - I'll run some more tests today with specific ammeter range results.

Not sure if the breaker was on or off when wire was disconnected - I'll retest today.  I did test with a new breaker - same results.

Thanks again - this one has me stumped!
« Last Edit: December 19, 2011, 10:55:46 AM by rb1204 »
Logged

Noam

  • Community Organizer
  • Hero Member
  • ***
  • Helpful Post Rating: 51
  • Posts: 2818

All - thanks for the help!!

The timer, one appliance module, and a light switch is on phase B.  The problem circuit, and one appliance module, is on phase A.  As a test, I moved the problem breaker to phase B, and had the same results.  The results are consistent - when the breaker is off, all appliance modules and light switch work, when the breaker is on, all work inconsistently (sometimes on/off commands work, most often they do not...).  I also ran these tests with all 220 breakers tripped (to try to eliminate any cross phase coupling by an appliance) - all results were the same.

Ammeter goes pretty low - I'll run some more tests today with specific ammeter range results.

Not sure if the breaker was on or off when wire was disconnected - I'll retest today.  I did test with a new breaker - same results.

Thanks again - this one has me stumped!

I had to do something similar a few years back (but my problem was with Insteon light switched on one circuit not responding to X10 signals at night - which turned out to have been due to my neighbor's noisy CFL bulb).

Here are my thoughts:
1. You tested with a new breaker, and got the same results. That probably rules out the breaker.
2. You moved the circuit to the opposite phase, and the results stayed the same. To me, it doesn't appear to be a phase-bridging issue.
3. Since the only thing left is the wiring on the circuit itself, perhaps there is some issue with the wiring (perhaps something isn't grounded well, or something along those lines). It could also be a transformer, or some other device wired into that circuit, that you just can't seem to find.
You may have to trace out how the circuit runs through your house (box-to-box), and try disconnecting it at each stage, to see if you can find where the problem starts. For example, if it runs like this:

Breaker box
Outlet 1
Outlet 2
Outlet 3
Light Switch
Light Fixture

I'd first disconnect it at the first outlet, and test with only the run from the breaker box to the first outlet connected to the breaker (with the outlet disconnected, and the line capped off for safety).
If it works fine at that point, then re-connect the outlet (with the other side disconnected), and test again.
Continue adding one segment at a time, until it stops working.
This will also give you an opportunity to check for other things connected to that circuit (doorbell transformer, perhaps?), that you weren't aware of.
Do you have any GFCI outlets on that circuit? One that is going bad might also produce noise.
What about illuminated light switches (you know, the ones with the little bulb inside to help you find the switch in the dark)? I suppose something like that could also put noise on the line.

If you can't get it working with ONLY the fist segment in place, you might want to see if you can go around that segment, perhaps using a length of Romex that you run (without fishing it - just for testing) from the breaker to the "outbound" side of that first box.

How far you go with testing this is a matter of how comfortable you are working with this (and from your posts it seems you are pretty comfortable), and how committed you are to fixing the problem.

Let us know if we can help further.