As long as it only turns on near the zero crossing, it can indeed control non-incandescent loads.
So, the bottom line is to only use dimmer modules to drive loads specifically designed to be used with dimmers. When deviating from this rule, be sure you understand exactly what you are doing to prevent failure of either the module or the device it is powering.
Jeff, a trifle disagreement with your first statement.
We use a lot of "accent lighting" in the home. One form is a series of "flameless" candles powered by two 3V DC transformer wall warts in the bedroom. I controlled these wall warts with two LM15A Socket Rockets, figuring they would be fine as the triac gating closely follows the sine, and dimming isn't possible.
When first trying the LM15A/wall wart combination I closely monitored the combination for problems, for a couple of days before tucking them behind a dresser and chest of draws. A couple of years later when one set of candles suddenly quit working, I paniced when I saw the wall wart with the plastic case completely deformed and melted down around the transformer which was now a beautiful smoked bronze color. I found the second wall wart to have the same symptoms, but it was still happily lighting it's candles. Two other identical wall warts, powering similar candles, but left on all the time, not switched with X10, were in like new condition. No evidence of any over heating.
Apparently the triac turn-on distortion of the LM15A was enough to cause the transformers to run slightly hotter than the plastic case could dissipate. I doubt there was ever enough heat developed to become incendiary. At least there was never any "burning tronics" odor that we could detect. And for reasons I will not elaborate on, I am very sensitive to, and well practiced at identifying said odor's.
I have replaced the two inductive wall warts with cheap cell phone chargers (over a year ago) and everthing seems happy.
But your sage advice of (paraphrasing): only use dimmer modules to drive loads specifically designed to be used with dimmers. When deviating from this rule, be sure you understand exactly what you are doing to prevent failure of either the module or the device it is powering."
Can not be over emphasized, to point of, even if you think it is OK, check it repeatedly for a while...