Today I found there was no hot water when I went to wash my hands. A quick check confirmed the hot water heater was fine, so something else was wrong.
Over a decade ago I set up a hot water recirculation loop to provide almost instant hot water at all faucets. The pump is controlled by an X10 lamp module that is switched on for about a minute every 15 minutes throughout the day to purge the lines. The pump worked fine when plugged directly into the outlet, so I suspected that the lamp module might have failed. Since we were getting ready to watch a movie, I planned to take care of it later.
Then the lights, equipment rack, and subwoofers would not respond to X10 commands. A quick check with my XTBM showed the noise level was .17Vpp at 120-124KHz, more than enough to block X10 operation. I plugged my prototype XTB-ANR into that outlet, and then the X10 modules responded to commands.
After the movie it only took a few minutes to track the strongest noise to the breaker panel. The only devices there are several old transformer style power modules and the PSC05 for the Rain8. I unplugged the PSC05, and noise level dropped to .01Vpp. Then I plugged the PSC05 back in with the Rain8 cable disconnected, and the noise level jumped back up. I swapped in a spare TW523, and everything is working again.
I took the bad PSC05 down to my workbench, and it pegs the XTBM noise reading when both are plugged into the same power strip. Obviously something in the PSC05 failed.
Jeff